So, at the moment 360s can only operate with one pan down (8 or 12) and max 75 mph North of Bedford.
I'm puzzled; will further overhead line work be necessary to get to the requirements of the new timetable (110 and all pans)?
Or is it because testing is needed to make sure that the OLE can cope with pans every 4 cars, which raises the question; why this has to be done empirically, rather than rely on design calculations and computer modelling?

Edit; couldn't spell 'Bedford' ...
 
Last edited by a moderator:
Sponsor Post - registered members do not see these adverts; click here to register, or click here to log in
R

RailUK Forums

Roast Veg

Established Member
Joined
28 Oct 2016
Messages
2,202
So, at the moment 360s can only operate with one pan down (8 or 12) and max 75 mph North of Bedford.
I'm puzzled; will further overhead line work be necessary to get to the requirements of the new timetable (110 and all pans)?
Or is it because testing is needed to make sure that the OLE can cope with pans every 4 cars, which raises the question; why this has to be done empirically, rather than rely on design calculations and computer modelling?

Edit; couldn't spell 'Bedford' ...
If a test train is damaged by incorrect modelling, it's cheaper to substitute it for another test consist than pay out for a broken passenger unit. It's also belt and braces.
 

Merle Haggard

Established Member
Joined
20 Oct 2019
Messages
1,979
Location
Northampton
If a test train is damaged by incorrect modelling, it's cheaper to substitute it for another test consist than pay out for a broken passenger unit. It's also belt and braces.

Thanks, fair enough. Unfortunately as well, 'the media' will pounce on any real or alleged shortcoming of railways even if innovation is involved.
 

Philip Phlopp

Established Member
Joined
31 May 2015
Messages
3,004
So, at the moment 360s can only operate with one pan down (8 or 12) and max 75 mph North of Bedford.
I'm puzzled; will further overhead line work be necessary to get to the requirements of the new timetable (110 and all pans)?
Or is it because testing is needed to make sure that the OLE can cope with pans every 4 cars, which raises the question; why this has to be done empirically, rather than rely on design calculations and computer modelling?

Edit; couldn't spell 'Bedford' ...

It's an updated OLE system so there's some additional testing to make sure the computer simulations and calculations are correct.

The design specification (3 x pantographs at 110mph, 2 x pantographs at 125mph, plus upgrade potential) for the MML once upon a time, a long long time ago, would have required the Series 1 OLE system, as found on the GWML, but as everybody now knows, it's "too heavy and complicated".

There has been an upgrade to the Series 2 OLE system (that which is found in the North West area and across the newly electrified routes in Scotland) to make it compatible with two of the three requirements (3 x pantographs at 110mph, 2 x pantographs at 125mph) and it has morphed into MS125, reflecting its place with the 'new' UK Master Series of electrification pick and mix systems.

The testing work using the DATS trainset is primarily to make sure the new MS125 system is doing as was predicted during the design and modelling stage, if it was normal new OLE installation, it would get no more attention than a quick sweep with the NMT or MENTOR, to confirm contact wire geometry/alignment, then a run with a couple of power hungry stock types to check the power supplies are working OK.
 

Merle Haggard

Established Member
Joined
20 Oct 2019
Messages
1,979
Location
Northampton
It's an updated OLE system so there's some additional testing to make sure the computer simulations and calculations are correct.

The design specification (3 x pantographs at 110mph, 2 x pantographs at 125mph, plus upgrade potential) for the MML once upon a time, a long long time ago, would have required the Series 1 OLE system, as found on the GWML, but as everybody now knows, it's "too heavy and complicated".

There has been an upgrade to the Series 2 OLE system (that which is found in the North West area and across the newly electrified routes in Scotland) to make it compatible with two of the three requirements (3 x pantographs at 110mph, 2 x pantographs at 125mph) and it has morphed into MS125, reflecting its place with the 'new' UK Master Series of electrification pick and mix systems.

The testing work using the DATS trainset is primarily to make sure the new MS125 system is doing as was predicted during the design and modelling stage, if it was normal new OLE installation, it would get no more attention than a quick sweep with the NMT or MENTOR, to confirm contact wire geometry/alignment, then a run with a couple of power hungry stock types to check the power supplies are working OK.

Thanks for that, too; I hadn't realised that the MML extension electrification was to a new spec. I should have - thankfully, the wires across Northamptonshire's landscape are supported by much less-visually-intrusive supports than the GWML's.
 

Nym

Established Member
Joined
2 Mar 2007
Messages
9,176
Location
Somewhere, not in London
It's an updated OLE system so there's some additional testing to make sure the computer simulations and calculations are correct.

The design specification (3 x pantographs at 110mph, 2 x pantographs at 125mph, plus upgrade potential) for the MML once upon a time, a long long time ago, would have required the Series 1 OLE system, as found on the GWML, but as everybody now knows, it's "too heavy and complicated".

There has been an upgrade to the Series 2 OLE system (that which is found in the North West area and across the newly electrified routes in Scotland) to make it compatible with two of the three requirements (3 x pantographs at 110mph, 2 x pantographs at 125mph) and it has morphed into MS125, reflecting its place with the 'new' UK Master Series of electrification pick and mix systems.

The testing work using the DATS trainset is primarily to make sure the new MS125 system is doing as was predicted during the design and modelling stage, if it was normal new OLE installation, it would get no more attention than a quick sweep with the NMT or MENTOR, to confirm contact wire geometry/alignment, then a run with a couple of power hungry stock types to check the power supplies are working OK.
MENTOR doesn't measure geometry, it measures the contact wire contact forces and position of the uplifted wire, at the speed at which it is being operated.
Only non-contact systems can measure geometry, but if it's a new OLE installation, it should be measured as part of the installation / commissioning of the OLE.

The IET and Desiro contact forces will behave rather differently to that of MENTOR. Particularly the IET pantographs which use the BW HSX design rather then the HSA or HSP designs that MENTOR uses. (And I believe the Desiro uses one of).

Instantaneous changes in contact force perform much better over 110mph on the HSX, and it is less venerable to multi pantograph operation problems.
 

Philip Phlopp

Established Member
Joined
31 May 2015
Messages
3,004
MENTOR doesn't measure geometry, it measures the contact wire contact forces and position of the uplifted wire, at the speed at which it is being operated.
Only non-contact systems can measure geometry, but if it's a new OLE installation, it should be measured as part of the installation / commissioning of the OLE.

The IET and Desiro contact forces will behave rather differently to that of MENTOR. Particularly the IET pantographs which use the BW HSX design rather then the HSA or HSP designs that MENTOR uses. (And I believe the Desiro uses one of).

Instantaneous changes in contact force perform much better over 110mph on the HSX, and it is less venerable to multi pantograph operation problems.

The position of the uplifted wire is an intrinsic part of the geometry of the entire OLE system though...

And I should have said geometry data is now more frequently being recorded now by the use of instrumented pantographs on passenger vehicles running at line speed (and to service patterns) rather than MENTOR running in a Q path.
 
Last edited:

Philip Phlopp

Established Member
Joined
31 May 2015
Messages
3,004
Which stocks are fitted with contact force OHL geometry measurement other than test trains?

I can understand non-contact camera systems being fitted to passenger units as it's just a single box on the roof, but a contact force system needs quite a bit more equipment.

There should be 1 x Class 390 with a full contact force measurement pantograph instrumentation system designed by DB ESG now in service, with the same (new) instrumentation as fitted to MENTOR. I thought there was another couple of units in service/coming into service with the same setup, but looking at the contract documentation, I think there was just two additional sets of instrumentation ordered to go onto MENTOR.
 

Energy

Established Member
Joined
29 Dec 2018
Messages
4,489
There should be 1 x Class 390 with a full contact force measurement pantograph instrumentation system designed by DB ESG now in service, with the same (new) instrumentation as fitted to MENTOR. I thought there was another couple of units in service/coming into service with the same setup, but looking at the contract documentation, I think there was just two additional sets of instrumentation ordered to go onto MENTOR.
Why are they using a 390 for this?
 

Philip Phlopp

Established Member
Joined
31 May 2015
Messages
3,004
Why are they using a 390 for this?

In addition to the reasons provided above - speeds, pathing, power demand, the Class 390 pantograph behaves rather differently to other pantographs, in that it moves opposite to the tilt of the carriage, to ensure the pantograph head remains correctly alligned with the contact wire, which introduces another potential dewirement risk which can't be picked up by any of the other contact or contactless catenary monitoring systems.
 

Domh245

Established Member
Joined
6 Apr 2013
Messages
8,426
Location
nowhere
There's no plan for a 390 to be used for testing the MML wiring however that I'm aware of?
 

Nym

Established Member
Joined
2 Mar 2007
Messages
9,176
Location
Somewhere, not in London
390s are one of, if not THE most power-hungry EMUs on the conventional network. They were used on both the Manchester - Liverpool and Euxton Jn - Manchester electrification schemes to check the power supply was adequate for a worst-case scenario IIRC.

Except that these OHL Geometry systems do not measure power draw or provide any kind of false load. The closest that they come is measuring the OHL voltage.

There's no plan for a 390 to be used for testing the MML wiring however that I'm aware of?

Nope, that's what the DATS 91s are being used for. I don't think they've been fitted with HSX pantographs though, so the 810s will still need homogenising.

Nor was one used on the GWML.

The 802s where extensively used on the GWML for geometry measurement.
 