The type of relay used to detect the lamp current has hysteresis. I don't have figures to hand, but the current for the armature to move to close the normally open / front contacts is higher than the holding current.Again, thanks for the interesting and detailed reply. I don't think the thing I saw a circuit diagram of was quite the same, but it was similar. However, the precise details don't matter - the important part is that these devices are designed to detect a filament lamp, which either takes a given current when it's working, or takes no current when it fails.
And the minimum holding current is part of the specification. Below this holding current value, it's a requirement for the normally open / front contacts to open. That is, if the signal is consuming less current than the specified minimum holding current, the GECR contacts will be open and hence the interlocking considers the signal to be unlit (or "black" to use the more common railway term).
Yes, LEDs have a multitude of failure modes including those you describe and a reduction of light output over time. I can't tell you exactly how the proving circuitry in LED signals works because that's not briefed out.
I can tell you that one failure mode of one make of LED signal head results in the signal being lit as brightly as normal, but consuming insufficient current to satisfy the minimum holding current for the GECR.
As part of routine maintenance, the S&T technician is supposed to check that the signal light output is sufficient. And this type of signal is only supposed to have a defined lifespan before the head or the LED module(s) in the head are renewed. The lifespan for the type I worked on was ten years.