This thread seems to have drifted away from one of the prime reasons suggested by the OP that our constrained structure gauge would benefit from a lower voltage. In theory that is true but in practice, there would be very little difference between the number of overhead clearances that needed significant civils. As I indicated inpost #17, most of the the clearance stated in the TSI, even with the RSSB easements allowed when accompanied with risk assessments, are dominated by the dynamic nature of catenary supported conductor wires.
The electrical dry-air flashover distance is approximately 1mm per kV, so for a 29kV ac maximum abnormal voltage, the flashover distance would be 41mm, compared to 3mm (3kV) or to 12mm (12kV) for a unique DC system. I doubt that an additional 38mm breathing space would significantly reduce the number of structures requiring modification. Indeed, the higher current of a lower voltage system would require a much higher current capability at each feed point (about eight times for a 3kV system), and that would require more substantial safety earthing on overhead structures to prevent them rising dangerously above earth. Furthermore, a DC supply also requires greater arc snubbing.